Skip Navigation

HVAC - Split Units

Started by Argo123
over 11 years ago
Posts: 44
Member since: Jan 2013
Discussion about
Hi, we had a Mitsubishi split unit installed in our unit. The HVAC guy also installed a condensing unit next to the split unit. This condensing unit makes a very loud noise lasting about 30 seconds every 5 minutes. Supposedly there is no other option but to just get used to this noise as the condensing unit is needed and has to be put next to the split unit. I have seen many split units in the past but don’t remember experiencing such loud noises coming from a condensing unit. Any thoughts, comments and advice would be greatly appreciated. Thank you in advance.
Response by NWT
over 11 years ago
Posts: 6643
Member since: Sep 2008

Usually there's a condensing unit outdoors and an air-handling unit indoors. Two pieces. Does your "also installed" mean there's a third unit?

Maybe if you tell us what the nameplates on the second or third units say, we can google it for you.

Ignored comment. Unhide
Response by Argo123
over 11 years ago
Posts: 44
Member since: Jan 2013

Slight correction - it is a condensate pump and not condensing unit next to the split unit.

Ignored comment. Unhide
Response by NWT
over 11 years ago
Posts: 6643
Member since: Sep 2008

Ah OK. There's no drain close enough for the condensate, so there's a pump to convey it there. Those are usually tin

Ignored comment. Unhide
Response by NWT
over 11 years ago
Posts: 6643
Member since: Sep 2008

y little motors, and only run when there's enough condensate to pump. I'd have the HVAC contractor start with that.

Ignored comment. Unhide
Response by uptown_joe
over 11 years ago
Posts: 293
Member since: Dec 2011

Agreed, the condensate pump can be replaced with a different (quieter) model. Might be helpful to get a larger pump/reservoir too; bigger motors are usually quieter and a larger reservoir would mean it runs less often.

There is also some possibility it could be relocated to an intermediate position between the indoor air handler and the final drain location -- the water would gravity-drain to a reservoir/pump at a more suitable intermediate location, and then be pumped to the final drain. So if there is a closet nearby it could be hidden there and muffled better. But it depends on your particular situation.

Ignored comment. Unhide
Response by flarf
over 11 years ago
Posts: 515
Member since: Jan 2011

Most split systems use a gravity drain to get rid of the condensate, so a pump isn't necessary.

If pumps are installed improperly (not fastened securely), cheap, or dirty, they'll be loud.

http://www.hvacquick.com/products/residential/Condensate-Pumps/Condensate-Removal-Pumps/Aspen-Mini-Aqua-Condensate-Pump-Kits

Ignored comment. Unhide
Response by flarf
over 11 years ago
Posts: 515
Member since: Jan 2011

I like uptown_joe's idea of moving the pump somewhere hidden. The pump will fail at some point and if you can move it somewhere out of the way (i.e. quiet) but still have it accessible for maintenance, that would be a good outcome.