Electric dryer vent_DOB rules
Started by reno_inuws
over 11 years ago
Posts: 6
Member since: Dec 2009
Discussion about
We are having a bit of trouble with approval for a vented electric dryer from our building's architect consulting firm. The W/D will be in the kitchen and vented through a non-functioning window (long been covered by cabinets). Our neighbors below have done this already. It has been suggested to us that venting in this way may violate DOB code, since it is less than 10 feet away from the window of... [more]
We are having a bit of trouble with approval for a vented electric dryer from our building's architect consulting firm. The W/D will be in the kitchen and vented through a non-functioning window (long been covered by cabinets). Our neighbors below have done this already. It has been suggested to us that venting in this way may violate DOB code, since it is less than 10 feet away from the window of our upstairs neighbor. Here is the relevant code from 2014. Can someone please help to clarify this issue for us, since there seems to be some confusion? Based on my reading, the 10 feet rule does not seem to apply to clothes dryers. 501.2.1 Location of exhaust outlets. The termination point of exhaust outlets and ducts discharging to the outdoors shall be located within the following minimum distances: 1. For ducts conveying noxious, toxic, explosive or flammable vapors, fumes or dusts including but not limited to exhaust form dry cleaning establishments and spray booths): 30 feet (9144 mm) from property lines; 10 feet (3048 mm) from operable openings into buildings; 6 feet (1829 mm) from exterior walls and roofs; 30 feet (9144 m) from combustible walls and operable openings into buildings which are in the direction of the exhaust discharge; 10 feet (3048 mm) above adjoining grade. Additional requirements may apply to Hazardous Exhaust Systems; see Section 510. 2.For other product-conveying outlets: 10 feet (3048 mm) from the property lines; 3 feet (914 mm) from exterior walls and roofs; 10 feet (3048 mm) from operable openings into buildings; 10 feet (3048 mm) above adjoining grade; 10 feet from any exterior fire escape , stair, or balcony. 3. For all environmental air exhaust outlets: 3 feet (914 mm) from property lines; 3 feet (914 mm) from operable openings into buildings for all occupancies other than Group U, and 10 feet (3048 mm) from mechanical air intakes. Such exhaust outlets shall not be considered hazardous or noxious. 4.Exhaust outlets and openings serving structures in flood hazard areas shall be installed in accordance with Appendix G oftheNew York City Building Code. 5. For specific systems see the following sections: 5.1.Clothes dryer exhaust, Section 504.4.... [less]
Add Your Comment
Recommended for You
-
From our blog
NYC Open Houses for November 19 and 20 - More from our blog
Most popular
-
20 Comments
-
19 Comments
-
25 Comments
-
52 Comments
-
25 Comments
Recommended for You
-
From our blog
NYC Open Houses for November 19 and 20 - More from our blog
It was 10 feet two years ago when I went through this. Why do you think it should be less? Your dryer vent isn't exactly environmental air exhaust...
The reference to 504.4 just adds additional information specific to clothes dryers (no screens, no screws, etc.). It doesn't mean clothes dryers are excluded from the requirements.
Ah. I thought they were not part of that category. I stand corrected. Thanks for that!
Hi, I am going thru the same thing, only our building architect said we have to be 4 feet away from from adjacent neighbors windows for a dryer vent.
I just looked it up to be precise. My window may be different as it is not subject to landmark approval, as it is on a back facade.
Under the mechanical code of NYC allows wall venting with the following provisions.
2 feet from any window opening within the same dwelling unit.
4 feet from any window opening of an adjoining dwelling unit (above as well as below)
10 feet from any air intake vent or public sidewalk
Mind you I have not been approved yet, as I am wanting to enlarge our kitchen and other things, however the above was the guidelines i was given.
Good luck, I understand persisting for a vent:)
Perhaps things have changed, but several years ago in NYC, electric dryers did not require exterior venting at all.
It would surprise me then, if there were regulations surrounding their venting if you so choose to do. Gas dryers, an altogether different story.
Alan, ALL dryers require venting unless they are those crap-o European-style "condensation" dryers.
... but not exterior venting. Those ridiculous water-bucket lint traps are (or were recently) a legal alternative for electrically-powered automatic drying machines.
"Those ridiculous water-bucket lint traps are (or were recently) a legal alternative for electrically-powered automatic drying machines."
They're not anymore.