Don't know why I didn't think of asking this before, but here it is: I live in a concrete condo. The floors, ceilings, interior and exterior walls are 12 inches of masonary, (it is blessedly quiet) the exterior is brick clad, whole thing well over 100 years old. The radiator bangs like a son-of-a- b!tch. To deal with it, I turn off the radiator at night, and on again in the morning. I've had... [more]
Response by alanhart
almost 15 years ago
Posts: 12397
Member since: Feb 2007
Ignored comment. Unhide
Response by front_porch
almost 15 years ago
Posts: 5316
Member since: Mar 2008

as apartment therapy pointed out, the banging is steam coming through water in the pipes. Your best solution for fixing that is not to train your super (or tear up your pretty floor) but to train your neighbors not to partially turn their steam valves (which is bad for the system and will eventually cause leakage anyway).

Side question: what do you mean you turn your radiator "off"? You're not playing with your steam valves are you?

Are the radiators being bled a couple of times a year? I'd start with that -- not yours, but your neighbors.

ali r.
DG Neary Realty

Ignored comment. Unhide
Response by alanhart
almost 15 years ago
Posts: 12397
Member since: Feb 2007

Don't forget to read through the comments on the AT thread ... there seem to be quite a few possible causes and (attempts at) solutions.

Ignored comment. Unhide
Response by needsadvice
almost 15 years ago
Posts: 607
Member since: Jul 2010

I am absolutely playing with the steam valves, I have no choice. I sounds like someone is whaling away on the pipe with a metal wrench, goes on for 5-10 minutes, and I can't sleep through that. I turn it ALL the way off (which takes about 5 full minutes of turning) and ALL the way on. Radiator was bled, tilted, pressure valves replaced etc., etc. Done it all. All of the other radiators are completely quiet and I love steam heat; gets so warm that I have to crack the window even if it's 10 degrees out. Love it.

But it's definitely the pipe in the floor.

How do I get the condo to fix it? If it's in the floor, it's not my pipe, is it?

Ignored comment. Unhide
Response by tina24hour
almost 15 years ago
Posts: 720
Member since: Jun 2008

Or, you can just give in to it!!!
http://www.studio360.org/blogs/studio-360-blog/2011/mar/09/radiator-symphonies/

Tina Fallon
Realty Collective, LLC

Ignored comment. Unhide
Response by drdrd
almost 15 years ago
Posts: 1905
Member since: Apr 2007

I haven't read the AT article 'though I certainly shall. I've found that the steam radiators always make a little bit of noise & I like that but we've got a new neighbor who has been putting too much water in her boiler & the pipes have been very noisy this winter & I've wondered if that was the reason.

Ignored comment. Unhide
Response by needsadvice
almost 15 years ago
Posts: 607
Member since: Jul 2010

Where is this AT article? What is AT?

@DRDRD: I had one plumber tell me the super is sending too much water up the pipe. The boiler is his responsibility. He had a bunch of professionals come and clean it last winter, and for a week there was no banging.

I wonder if the professionals fed it the right amount of water, and that's what fixed it . . .

It would be ironic, but typical, if I have the floor torn up, jackhammers in the bedroom, and get it "fixed" only to find out it's the idiot super putting in too much water.

Ignored comment. Unhide
Response by needsadvice
almost 15 years ago
Posts: 607
Member since: Jul 2010

I am caught up in the love/hate relationship that is Pre-war apartment living. . .

Ignored comment. Unhide
Response by vic64
almost 15 years ago
Posts: 351
Member since: Mar 2010

In most cases, try not to shut the radiator when steam is coming in despite the noise. If you shut the radiator, the steam would be trapped inside the radiator and condenses to water. Water can rusts metal and creates clogs and leaks down the road.

Ignored comment. Unhide
Response by truthskr10
almost 15 years ago
Posts: 4088
Member since: Jul 2009

Thought this thread was about some new fetish, sounded painful.

Ignored comment. Unhide
Response by OTNYC
almost 15 years ago
Posts: 547
Member since: Feb 2009

Call me crazy but I enjoy the banging. That said, I have 2 little kids who ensure I am awoken every 3 hours; at least with the radiator, I can stay in bed and know it will eventually stop. Babies, not so much.

Ignored comment. Unhide
Response by OTNYC
almost 15 years ago
Posts: 547
Member since: Feb 2009

Truth - thanks for making me laugh. I think Savage wrote a column on "radiator banging" in his Voice column...

Ignored comment. Unhide
Response by Sunday
almost 15 years ago
Posts: 1607
Member since: Sep 2009

I'm going to pretend I'm above this kind of a respond...

needsadvice, after reading your other posts, I have to ask... What's the matter, you can't afford to buy a place at an uber-prime building that doesn't have these kind of problems?

Ignored comment. Unhide
Response by Sunday
almost 15 years ago
Posts: 1607
Member since: Sep 2009

I'm NOT going to pretend I'm above this kind of a response...

Ignored comment. Unhide
Response by igabi
almost 15 years ago
Posts: 1
Member since: Feb 2011

had the same problem in a triplex (small home in qns). the letoff valve/drain needs to be "bled" while the system has some pressure (it's water at 99-100 celsius).lots of junk will come out.bleed it (or ur super) til clear; you may also look at your valves and replace/clean if old/clogged; you'll be fine for 1-2 weeks.then repeat... splurge on a minisplit if allowed, w/ heating abilities.quiet and reliable.

Ignored comment. Unhide
Response by jas
almost 15 years ago
Posts: 172
Member since: Aug 2009

We recently did what vic64 advised not to do. Have a $1,000 bill to fix my neighbor's ceiling from the resulting water damage-- first quote was for a heart-stopping $8,000!!! Was advised by the plumber to do as front porch recommended.

Ignored comment. Unhide
Response by drdrd
almost 15 years ago
Posts: 1905
Member since: Apr 2007

The water level has to be monitored & maintained & therefore the level can vary. If you have a one pipe steam radiator, the radiator must be lower on the end with the pipe & the other end of the radiator can be raised with wooden blocks or wedges, thereby allowing the ccoled steam, now water, to return to the boiler to be reheated.

Ignored comment. Unhide
Response by needsadvice
almost 15 years ago
Posts: 607
Member since: Jul 2010

@vic64: No, I turn it off when it's completely quiet, well in advance of the action.

@Sunday: LOL! Just because I can, doesn't mean I will. For 5 minutes of turning a valve, I'll pocket the extra money.

@DRDRD: The thing is tilted at a 20 degree angle to incoming pipe. I think the building has settled and the pipe branching off the main pipe no longer tilts, so it holds a ton of water. Or it's the idiot super.

So, from all these responses I guess nobody knows how to get a condo to repair something?

I recently replaced a window, because they said the windows are mine. Now that I think about it, that sounds like bull too . . .

What does a condo own, and what does the owner own?

Ignored comment. Unhide
Response by front_porch
almost 15 years ago
Posts: 5316
Member since: Mar 2008

jas: unfortunately I speak from experience. I did the same thing at my beach house and created a leak in my front hall ceiling. I think it took the third plumber to explain to me that I was being an idiot.

needs advice -- AT = the apartment therapy blog. Also, I know it's loud, but you shouldn't be touching those valves. As noted, when you close them, are just creating water to live in that joint and bother you, aside from anything your idiot super is doing.

Sounds like taking out this one pesky radiator might be an even better solution.

ali r.
DG Neary Realty

Ignored comment. Unhide
Response by needsadvice
almost 15 years ago
Posts: 607
Member since: Jul 2010

@ALI- That's not a bad idea! Take that puppy out! There's heat to spare in the place.

Or maybe remove it, seal it off, and put in a new one that taps into the vertical pipe, at a point above the floor.

I bet if I threaten to mess with the big vertical pipe, the condo will pay some attention . . .

Ignored comment. Unhide
Response by Sunday
almost 15 years ago
Posts: 1607
Member since: Sep 2009

needsadvice: "For 5 minutes of turning a valve, I'll pocket the extra money."

That's poor people talk.

Ignored comment. Unhide
Response by front_porch
almost 15 years ago
Posts: 5316
Member since: Mar 2008

NA, either of those solutions can be discussed with the condo -- but I like 'em both because they both spare your pretty floor.

ali r.

Ignored comment. Unhide
Response by Reno09
almost 15 years ago
Posts: 45
Member since: Jan 2009

Needsadvice - First, I would find out if you have a 1 pipe or 2 pipe system. If it's a 1 pipe, that means that the steam travels up and the condesate (i.e. the water by-product that forms after steam cools) travels down the same pipe. If it's a 2 pipe, then they travel in different pipes. I have a 1 pipe and recently had the same problem. Here are the possible reasons I was told for the noise:

1. Too much water in the boiler
2. Boiler run at too high of a pressure, which pushes the condesate (i.e. water by-product that forms in your radiator as the steam cools and is supposed to drain back to the boiler) back up instead of allowing it to drain
3. Other radiators off the same riser can be putting water back in the pipes. One possible cause is if they don't have the valves turned all the way off or on. You can't adjust the heat/temperature by turning the valve, but some neighbors don't seem to realize this.
4. Riser has water in it, needs to be drained
5. Return (i.e. pipe that goes back to the boiler) needs to be cleaned, maybe there's a clog?
6. Boiler might not be producing "clean" steam - i.e. it hold more moisture than it should. Recommended to add detergent to the boiler

Ignored comment. Unhide
Response by 875gator
almost 15 years ago
Posts: 193
Member since: Sep 2010

How much does it cost to replace the average radiator? Please, no 'it depends' qualifiers.

Ignored comment. Unhide
Response by Sunday
almost 15 years ago
Posts: 1607
Member since: Sep 2009

$875

Ignored comment. Unhide
Response by drdrd
almost 15 years ago
Posts: 1905
Member since: Apr 2007

$23.95

Ignored comment. Unhide
Response by alanhart
almost 15 years ago
Posts: 12397
Member since: Feb 2007

Pay what you wish ... you must pay something.

Ignored comment. Unhide
Response by birdier
almost 15 years ago
Posts: 50
Member since: Nov 2008

depends how many British Tiny Udders (BTUs) the rating unit radiates; in a whey, size matters

Ignored comment. Unhide
Response by 875gator
almost 15 years ago
Posts: 193
Member since: Sep 2010

Whey?